Yahoo Message Number: 96755 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96755)
I am in Sturgis and only have 30 amp every time I try to run two airs it trips the circuit breaker on my whole house board it shows 110 volts and 3 or 4 amps does anyone know what that means. if I am only pulling 3or 4 amps it should run two airs I will post a picture of the display Thank you in advance
Marvin Hardy 2008 Intrgue #12249
Yahoo Message Number: 96756 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96756)
For two A/Cs 50 amps. Shut off one A/CSent from Yahoo Mail for iPhone From:
Marvin Hardy twotendriver@... [Country-Coach-Owners] ; To:
Country-Coach-Owners@yahoogroups.com ; Subject:
[Country-Coach-Owners] power [1 Attachment] Sent:
Fri, Aug 1, 2014 9:18:06 PM
[Attachment(s) from Marvin Hardy included below] I am in Sturgis and only have 30 amp every time I try to run two airs it trips the circuit breaker on my whole house board it shows 110 volts and 3 or 4 amps does anyone know what that means. if I am only pulling 3or 4 amps it should run two airs I will post a picture of the display Thank you in advance Marvin Hardy 2008 Intrgue #12249
Yahoo Message Number: 96757 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96757)
I would expect it to be able to run both a/c as long as they don't both start at the same time, this is what an ems does is stage them so they don't both hit with startup surge at same time.
Ray
They say wine improves with age! As I enter my golden years, I say age improves with wine! The Born Loser
Yahoo Message Number: 96758 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96758)
If your batteries are up to snuff, all the lights turned off, the floor off, TV's off, and the refer on propane you had the old 13.5 K btu airs you could run both airs with low fan on moderately warm days. But with
the new 15K btu airs you have there is no way to run two airs at the same time on 30 amps. I was at a
park that only had 20 amp breakers and I had trouble operating one air and 1 TV with the refer on
propane.
TWI 2004 Intrigue 11731
Original email:
-----------------
From: James Spivey reeljr65@... (reeljr65@...) [Country-Coach-Owners] Country-Coach- Owners@yahoogroups.com (Owners@yahoogroups.com) Date: Fri, 1 Aug 2014 14:25:01 -0700 To: Country-Coach-Owners@yahoogroups.com (Country-Coach-Owners@yahoogroups.com) Subject: RE: [Country-Coach-Owners] power
For two A/Cs 50 amps. Shut off one A/C href="https://overview.mail.yahoo.com?.src=iOS" (https://overview.mail.yahoo.com?.src=iOS)>
Sent from Yahoo Mail for iPhone
mail2web.com Enhanced email for the mobile individual based on Microsoft Exchange - http://link.mail2web.com/Personal/EnhancedEmail (http://link.mail2web.com/Personal/EnhancedEmail)
Yahoo Message Number: 96759 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96759)
Marvin,
I don't think you'll successfully run two air conditioners on that 30 amp line. The voltage is too low.
With voltage at 110 with only two amps you are likely to be at somewhere near 107 volts with the first A/C running. That will put you at the original 2 amps plus probably 14 amps for the A/C. The second A/C would draw the voltage further to more like 104 volts as the A/C tries to start. I just don't think that second A/C is going to work.
Good luck.
George in Birmingham(still in Santa Fe) '03 Magna 6298
Yahoo Message Number: 96760 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96760)
Marvin, I can't run both on 30. You'll need to turn one off or run them off your generator.
Jock Vargo2005 Inspire51428
Yahoo Message Number: 96761 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/96761)
Tired it the other day and I would have to agree, only run one A/C at a time.
Wally & Elta Mae
2007Allure 470 #31535