I'm plunged into 50A service and only have 30A on my meter in the hall. If the power gets over loaded it shuts down the water heater, washer dyer and so on. I believe the shuting down is correct but does anyone have any idea why I only have 30A. I cked the plug and have 120 volt on both legs and the surge protector reads power to both sides.
Craig
2005 37 ft Allure
31256
Yahoo Message Number: 99745 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/99745)
What voltage do you see when you measure between both hot legs? Should be 240 if wired correctly.
Ray O
---
Yahoo Message Number: 99746 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/99746)
Craig I was told by Country that that was 30 amps per leg, my silver leaf only goes to 30 amp also Darrell
2007 Intrigue
---
Yahoo Message Number: 99748 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/99748)
If L1 and L2 are in phase, meaning the voltage across them is 0 then the load device will think you are on 30 amp. Measure the voltage across L1 and L2, it should be 240.
Let us know
Mikee
Yahoo Message Number: 99751 (http://groups.yahoo.com/neo/groups/Country-Coach-Owners/conversations/messages/99751)
Check your Main circuit breaker. Could have one leg of it dead. Not likely but it would be something I wold check if I was plugged into 50 amp and was only getting 30 amps inside the coach.