GFI

Yahoo Message Number: 26606
Interesting, although not too tough of a problem.

GFI in bathroom tripped and continued to trip immediately when reset.

Followed the circuit downstream, in this case toward the galley. The second receptacle downstream had the loose ground connection.

For reference, these are the push in type ground connections (like a cloths-pin)on the back of the receptacle.
The stripped wire must be securely squeezed between the clips on the connector. Don't like them real well, but they would need to be replaced with a different type to change the connection.

Regards
Ray and Rue

054 Allure 31176