Topic: Power loss on 30 amp (Read 775 times) previous topic - next topic
0 Members and 1 Guest are viewing this topic.

Power loss on 30 amp

Yahoo Message Number: 88896
Been plugged into 30 amp, service for 4 days and everything was good. Refer on propane and only running 1 AC when needed. Move the coach today to get better satellite and replugged into same 30 amp, same outlet. Now nothing to the microwave or the audio system. Checked all breakers, fuses, circuits. Checked surge guard and have 30 amp, since floor heat, refer, will run with inverter off. Still no power to other and outlets. Suggestions on where to check next. I'm out of ideas.
Roger Harper
2006 Intrigue
#11990


Re: Power loss on 30 amp

Reply #2
Yahoo Message Number: 88898
Transfer switch is making the clicking sound when the power starts; are there any checks for it? I thought if the transfer switch was bad, we wouldn't get ANY power to the coach. We are getting power, but only to selected areas.

Roger Harper
2006 Intrigue
#11990


Re: Power loss on 30 amp Update

Reply #4
Yahoo Message Number: 88901
Now when I reset my Xantrex 2000 and turn on the inverter, I get an AC back feed warning to fix immediately. Consulted the manual, but no guidance there. Any ideas where I should start?

Roger Harper
2006 Intrigue
#11990

Re: Power loss on 30 amp

Reply #5
Yahoo Message Number: 88903
Check, reset, both GFIs. Check voltage out, with a meter, on both sides of the T-Switch.

Jim 07 Allure #31570

Re: Power loss on 30 amp Update

Reply #6
Yahoo Message Number: 88904
No idea about the inverter, do things work if you run on the genset?

Jim

Re: Power loss on 30 amp

Reply #7
Yahoo Message Number: 88905
When my AC outlet plugs went out it was caused by the circuit breaker on the inverter (a little black button) being tripped. Once reset, all was well.

Larry, 03 Allure, 30856

Re: Power loss on 30 amp Update

Reply #8
Yahoo Message Number: 88908
Sent: Sunday, June 23, 2013 4:40 PM Subject: RE: [Country-Coach-Owners] Re: Power loss on 30 amp
Start the generator, the Transfer switch should change over and prioritize the generator. If that does not work check voltage on red and white wire going in to transfer switch. If you have power, next check power leaving the switch. If you have power leaving the swich it should be working. Transfer switches are very expensive, I don't think that is your problem. Good luck Tom Buka 1996 affinity 48,000 miles Cat 350hp Sent from my ASUS Eee Pad

Roger Harper wrote:

Now when I reset my Xantrex 2000 and turn on the inverter, I get an AC back feed warning to fix immediately. Consulted the manual, but no guidance there. Any ideas where I should start? Roger Harper
2006 Intrigue
#11990

Re: Power loss on 30 amp

Reply #9
Yahoo Message Number: 88916
Roger, check the GFI receptacle. sounds like just your outlets are down. On my Inspire, its located in the inboard side of the china cabinet just aft of the DS slide. good luck.

Jim Hodges

2007 Inspire 360
#51969



A gun is like a parachute. If you need one, and don't have one, you'll never need one again.

The strongest reason for the people to retain the right to keep and bear arms is, as a last resort, to protect themselves against tyranny in government........ Thomas Jefferson

An armed man is a citizen. An unarmed man is a subject. Only a government that is afraid of its citizens tries to control them. Anon.


Re: Power loss on 30 amp

Reply #10
Yahoo Message Number: 88924
Roger- you have 2 transfer switches, one "main" that distinguishes incoming shore from incoming gen, and one in the inverter that switches between outgoing-incoming 120v and outgoing-inverted 120V. If you have shore or gen, the inverter's xfer uses it to charge & to turn around to the 120V out. If no 120V in, the inverter's xfer & other electronics inverts 12V into 120V & sends it out.
The inverter xfer failing may indicate (along w/the error message you are receiving) a problem w/internal electronics.
The following have experience at Xantrex repair, otherwise the Xantrex party line is "buy a new one": Don Wheeler, Mt. Hood OR 503-928-0407 Pat Fuge, SanDiego CA 619-992-5932 Also in the inverter repair business: Ernie Foley, Richmond CA 510-235-8752 Jim Lewis Infinity Coach, Sumner WA 253-891-0879 Good luck, let us know how it turns out. Mike

Re: Power loss on 30 amp Update

Reply #11
Yahoo Message Number: 88926
If refer will run, you have shore power through the transfer switch to the coach.
If items that will not run all are outlet driven, check your GFI outlets, reset the panel breakers for the outlets and check the breakers on the Inverter. With power to the coach (refer) you do not need the inverter on.

Dean

95 Magna 5280

Re: Power loss on 30 amp Update

Reply #12
Yahoo Message Number: 88949
Checked the transfer switch both with shore and genset; checked out fine. Hard reset on inverter failed to get it online. Will be replacing the inverter tomorrow,

Roger Harper
2006 Intrigue
#11990