Magnum 2000 charger/inverter

Yahoo Message Number: 71474
I am concerned about my Magnum 2000 charger/inverter in that the fan(s) seem to now run constantly. I dont recall this being the case earlier in the year. The battery, transformer, and FETs temps are 60C the fans are supposed to run as I understand it. Resetting and powering down have not helped. The unit seems to be functioning normally otherwise. Any suggestions would be greatly apprecited. thanks
mark

2008 Tribute 260
#81131

 

Re: Magnum 2000 charger/inverter

Reply #1
Yahoo Message Number: 72901
Follow-up: While Magnum Inverters/Chargers are great..they do break down occasionally. In my case, the FETs board went haywire and caused the 2 cooling fans to run constantly on high. New FETs board...problem solved. Robert at "the 1 Stop Custom Shop" in Colorado Springs found/fixed the problem. While his main focus is inverters/chargers/electrical stuff...he does many other things for motorhomes. I will go back to him for other maintenance/service issues/work on my CC.