Topic: Onan 6.5 Lp gas Marquis generator (Read 949 times) previous topic - next topic
0 Members and 1 Guest are viewing this topic.

Onan 6.5 Lp gas Marquis generator

Yahoo Message Number: 95082
My son owns a 1997 Intrigue with Onan LP generator. Several weeks ago the utility circuit developed intermittent low voltage, the air conditioners, refrigerator circuits all were steady at 120v ac. This corrected itself for a few weeks and then generator output failed totally. Generator engine runs smoothly but no output at all to transfer switch. zI am trying to help him and thanks in advance for any advice. David White 99 Allure 30349. (with the great power tech diesel gen)

Re: Onan 6.5 Lp gas Marquis generator

Reply #1
Yahoo Message Number: 95090
Replace the brushes, clean the slip rings, then test - if still no power, then ohm out the rotor & stator, if all that is good then voltage regulator. Usually when the reg starts to go bad the voltage will be unsteady depending on amount of load
Just did 2 this week, one was a bad stator $800 the other was a bad regulator $550

Good luck!
Jim

Infinity Coach

 

Re: Onan 6.5 Lp gas Marquis generator

Reply #2
Yahoo Message Number: 95278
Copy, thanks for the help! I am thinking it might be the regulator, but we will see soon enough. We will post the end results to aid anyone else encountering this same issue. Thank you again and hi dad!

Jesse White 97 Intrigue (with the not-so-great 6500 Onan LP generator) ha ha