Topic: House batteries 3 amp draw (Read 595 times) previous topic - next topic
0 Members and 1 Guest are viewing this topic.

House batteries 3 amp draw

Yahoo Message Number: 20632
John

3 Amps and everything that you can shut off was off. Had the switch at the door off and the inverter. If you check out the wiring and also the drawing you will find that the isolater switch inside the door only isolates the inside of the coach. ( domestic disconnet ). There are 3 other systems or circuits that remain hot on the house battery wiring plus the inverter. 1. Generator start 2. HWH leveling system 3.
Ignition relay ( Cross battery start / echo charger ) The echo charger is working correctly, so that should not be an issue. The answer from CC about the draw was "you need to keep it plugged in". They did not seem surprised that there was such an issue nor were they going to trouble shoot the problem. I will check a couple more things to see if I can find it, but I got the problem fixed with the manual shut off switch. I believe all other CC models have manual shut offs for the house batts.
Ned