Re: No Power at Generator panel
Reply #6 –
Yahoo Message Number: 114231
Your 2000 Affinity is probably similar to my 2000 Magna and all locations I talk about are based on my coach; 40 feet, no tag.
Did you check the 12 volts to the generator by measuring from the positive connection at the generator and chassis ground? You might have a bad ground running to the generator.
Assume you have 12 volt house voltage inside the ooach. If not, there is a 200 amp breaker in the compartment behind the battery bay or in the battery bay itself. Check that breaker and check for power at both sides of the breaker. From that breaker there is a wire running to the electrical bay that is attached to the house battery disconnect solenoid. The generator gets its power from the hot side of that solenoid through a 105 amp circuit breaker.
The house battery disconnect solenoid and 105 amp circuit breaker for generator power is in the electrical bay forward of the first compartment. I have to remove a panel from the forward wall of that compartment to access the electrical bay.
If the breaker is not tripped, check for voltage on both sides of the breaker to make sure you are getting voltage to that point.
Let us know what you find.
pete
2000 40' Magna CAT C-10, #5892