AC Condensation leak

Yahoo Message Number: 81394
One AC unit is dripping condensation onto the floor. Duo- Therm model, Penguin # 620515. They (Duo-Therm Dometic) recommend after extensive testing, option 7 or 8 with details drawings. Wondering if anyone has done or had either options performed?
The water is,I think, being pulled off the evaporator coil by the fan. The water drips from the fan blower side. So, I assume, the drip pan is not the issue. Water does flow freely from the top of the coach from drains on each side. Tried using lower fan speed and leaving the fan on manual. This may help along with lower humidity.

Thanks for any reply.

Paul Cummings,

01' Intrigue, # 11309

Re: AC Condensation leak

Reply #1
Yahoo Message Number: 81401
I had that experience. The mounting bolts for the AC unit had been over-tightened at the factory, and had distorted the gasket, which was replaced and fixed the problem.

Phil Webb, '06 Inspire 51836