Re: All Batteries Appear to be Out-Gassing and Sweating -- WORRIED
Reply #3 –
Great info - directionally I suspect the solar controller may need its settings adjusted to drop to a lower voltage 13.4V max, even 13.2 to provide a lower float voltage and prevent off gassing.
The Magnum inverter/charger is fine, max AC connection of 30A is correct - I believe it only has a 30 breaker feed/pass through max capability anyhow. No diff if you are connected to 50A or 30A shore power.
Equalization is a high voltage period (greater than 15V) for 15 minutes to deliberately put the batteries into a boil situation which "mixes" the electrolyte solution (poor analogy but it equalizes electrical charge across the entire battery). Lifeline are the only AGM battery that I am aware of that recommends a periodic equalization - I have always manually initiated an equalization step, and have not done any with my current AGM (Discover Energy brand).
Shutting off all 12V simply means shutting down fridge, furnace, lights, dash loads (GPS, radio etc). Shutting off disconnects "May" isolate batteries from chargers (MAgnum and Solar) depending on how it was wired. Batteries should be confirmed they are at full charge.
Hope this helps,
Brian
PS _ You can clean up your batteries with baking soda dissolved in water and lots of fresh water rinse. That way you can monitor after you reduce solar charger float voltage.
EDIT: You may want to consider shutting off the solar charging while you are plugged in to shore power - The Magnum charger is a great charger and will keep all 12V and batteries running fine without Solar. Solar can be enabled when you are boondocking, or in storage without shore hookup. Again I would reduce solar charge voltage to 13.4V max.